I have two TSTATCCPS701 carrier Programmable Thermostats, one in downstairs and another upstairs for my heat pump system. I replaced the two TSTATCCPS701 with T1800 Venstar thermostat (https://shop.rfwel.com/venstar-t1800...hermostat.html) which look identical. The wiring is also identical (see photos) except that the TSTATCCPS701 carrier thermostats do not have jumpers. With the jumpers set according to the diagram in the manual page 5.4 (https://wdi.rfwel.com/cdn/techdocs/T...stallation.pdf) I set the temperature down 10 degrees for cooling (it's was a warm day) and got no response. Both the air handler fan and the heat pump did not come on. So I switched the J1 jumper to the upper two pins and that got the air handler to come on, but the heat pump still did not come on. Any ideas on this?